π₯ Loss on Ignition (LOI) Test of Cement
π Purpose
The Loss on Ignition (LOI) test determines the amount of volatile substances (mainly moisture, COβ, and organic matter) lost when cement is heated to a high temperature. It is a measure of cementβs stability, freshness, and proper storage condition. The test helps identify deterioration due to prolonged exposure to air and moisture.
π Reference Standard
- IS 4032:1985 β Methods of Chemical Analysis of Hydraulic Cement
- IS 269:2015 β Specification for Ordinary Portland Cement
π§ͺ Apparatus Required
- Porcelain or platinum crucible
- Analytical balance (accuracy Β±0.001 g)
- Muffle furnace capable of maintaining 900 Β± 50Β°C
- Desiccator
- Tongs and gloves
βοΈ Procedure
- Weigh about 1 g of cement sample and record it as Wβ.
- Place the sample in a clean, dry crucible.
- Heat the crucible in a muffle furnace at 900 Β± 50Β°C for 15 minutes.
- Remove and cool it in a desiccator for 30 minutes to prevent moisture absorption.
- Weigh the cooled sample again and record as Wβ.
π Formula
Loss on Ignition (LOI) % = ((Wβ β Wβ) / Wβ) Γ 100
Example:
If the initial weight (Wβ) = 1.000 g and the final weight (Wβ) = 0.952 g, then:
LOI = ((1.000 β 0.952) / 1.000) Γ 100 = 4.8%
π Permissible Limits (as per IS 269:2015)
| Type of Cement | Maximum LOI (%) |
| Ordinary Portland Cement (OPC) | 5.0% |
| Portland Pozzolana Cement (PPC) | 5.0% |
| Portland Slag Cement (PSC) | 4.0β5.0% |
π Interpretation of Results
- LOI β€ 5% β Cement is fresh and stable.
- LOI > 5% β Indicates deterioration or carbonation due to improper storage.
π§ Significance of LOI Test
- Ensures cement has not absorbed moisture or COβ during storage.
- Helps identify expired or damaged cement batches.
- Indicates presence of unburnt fuel or organic matter in manufacturing.
β οΈ Causes of High LOI
- Prolonged exposure to atmosphere (moisture absorption).
- Incomplete burning of raw materials during clinker formation.
- Presence of uncombined calcium hydroxide (Ca(OH)β) or carbonates (CaCOβ).
- Contamination during packaging or storage.
β
Precautions
- Use a clean, dry crucible.
- Maintain proper furnace temperature (900 Β± 50Β°C).
- Cool in a desiccator immediately after heating.
- Handle the sample with tongs to avoid contamination.
π Conclusion
The Loss on Ignition test is an important chemical test to assess the quality and soundness of cement. A high LOI value indicates old or deteriorated cement, while a low value confirms freshness and proper manufacturing. For Ordinary Portland Cement, the LOI should not exceed 5% as per IS 269:2015.