πŸ”₯ Loss on Ignition (LOI) Test of Cement

πŸ” Purpose

The Loss on Ignition (LOI) test determines the amount of volatile substances (mainly moisture, COβ‚‚, and organic matter) lost when cement is heated to a high temperature. It is a measure of cement’s stability, freshness, and proper storage condition. The test helps identify deterioration due to prolonged exposure to air and moisture.

πŸ“˜ Reference Standard

  • IS 4032:1985 – Methods of Chemical Analysis of Hydraulic Cement
  • IS 269:2015 – Specification for Ordinary Portland Cement

πŸ§ͺ Apparatus Required

  • Porcelain or platinum crucible
  • Analytical balance (accuracy Β±0.001 g)
  • Muffle furnace capable of maintaining 900 Β± 50Β°C
  • Desiccator
  • Tongs and gloves

βš™οΈ Procedure

  1. Weigh about 1 g of cement sample and record it as W₁.
  2. Place the sample in a clean, dry crucible.
  3. Heat the crucible in a muffle furnace at 900 Β± 50Β°C for 15 minutes.
  4. Remove and cool it in a desiccator for 30 minutes to prevent moisture absorption.
  5. Weigh the cooled sample again and record as Wβ‚‚.

πŸ“ Formula

Loss on Ignition (LOI) % = ((W₁ βˆ’ Wβ‚‚) / W₁) Γ— 100

Example:

If the initial weight (W₁) = 1.000 g and the final weight (Wβ‚‚) = 0.952 g, then:

LOI = ((1.000 βˆ’ 0.952) / 1.000) Γ— 100 = 4.8%

πŸ“Š Permissible Limits (as per IS 269:2015)

Type of CementMaximum LOI (%)
Ordinary Portland Cement (OPC)5.0%
Portland Pozzolana Cement (PPC)5.0%
Portland Slag Cement (PSC)4.0–5.0%

πŸ“ˆ Interpretation of Results

  • LOI ≀ 5% β†’ Cement is fresh and stable.
  • LOI > 5% β†’ Indicates deterioration or carbonation due to improper storage.

🧭 Significance of LOI Test

  • Ensures cement has not absorbed moisture or COβ‚‚ during storage.
  • Helps identify expired or damaged cement batches.
  • Indicates presence of unburnt fuel or organic matter in manufacturing.

⚠️ Causes of High LOI

  • Prolonged exposure to atmosphere (moisture absorption).
  • Incomplete burning of raw materials during clinker formation.
  • Presence of uncombined calcium hydroxide (Ca(OH)β‚‚) or carbonates (CaCO₃).
  • Contamination during packaging or storage.

βœ… Precautions

  • Use a clean, dry crucible.
  • Maintain proper furnace temperature (900 Β± 50Β°C).
  • Cool in a desiccator immediately after heating.
  • Handle the sample with tongs to avoid contamination.

πŸ“˜ Conclusion

The Loss on Ignition test is an important chemical test to assess the quality and soundness of cement. A high LOI value indicates old or deteriorated cement, while a low value confirms freshness and proper manufacturing. For Ordinary Portland Cement, the LOI should not exceed 5% as per IS 269:2015.